Alan asked if the inspector should accept or reject the installation in Indiana. I say not if some other code requires it.
If using the IRC or IBC, illumination is required if there is less than 8% glazed area per floor area exists. Stairway illumination is required with different switching reqs depending on the location of the stairs.
Saying the NEC doesn't require it -end of story-- is not an acceptable or responsible or complete answer.
I know this is an electrical contractors site, but all codes that relate to electrical work, not just the NEC, can and should be applied to the electrical contractor.
But yes, more than 8% glazed area does not require any type of artificial illumination per IRC or IBC(except egress paths with exceptions).
Alan should check his adopted building code and check for amendments. If the I-codes are adopted then make sure there is a light and ventilation schedule on the plans to verify whether artificial illumination is required.
We are not bound (or trying) to only discuss electrical code requirements from the NEC on this board, right?