I don't see anything in section 230.70 that would require a disconnect at the pole. I have seen a lot of curbside meters, especially in rural service, that supplied service equipment located clean out of sight from the meter. Utilities require meters on poles so that they do not have to enter the property to read them. The location of the meter does not govern the location of the service disconnecting means. A good example is the yard pole or pedestal very commonly found on agricultural properties. The metering occurs at the pole to facilitate the use of a single meter for the entire premise. The service disconnecting means can then be located either at the meter or on each building.

If you do decide to locate the service disconnecting means at the pole you will still have to locate the building disconnecting means at each building. In the event that there are conductive pathways between those buildings you would be required to run an equipment grounding conductor with the feeder to each building. This will markedly raise the cost of the installation.
--
Tom H


Tom Horne