I would question why you needed the disconnect for the garage at the house and the 4 wire feeder to the garage in the first place. Why not just have the disconnect at the garage fed with 3 wire USE and SE running top the disconnect in the house?
That looks like the "Maypole" setup we see a lot around here. If the meter was on a post there wouldn't be a question IMHO.I don't see hanging on the house changing that much if the SEC to the garage left immediately.
I do agree that in an emergency situation a fireman might assume that was the house disconnect. They don't usually stop and read signs if they think they know what they are doing. That is all the time


Greg Fretwell