I have an overhead service install. We have a double lug, 320 meter can.

I came out of the meter to a disconnect, then ran 4 conductor to a detached garage panel. - no problems here.

Heres the problem - I came out of the meter again with only 3 conductors. I ran this wire outside the building 20 feet, then came into the building and immediately into the back of the panel.

The inspector says I need a disconnect at the meter for that panel? I have always heard I could theroretically run the SE cable around the building twice without a disconnect, as long I immediately enter the panel.

He refrenced 230.2, saying it is confussing if they need to interrupt the service. We offered to have a plaque made identifying, denoting the feeders supplying each building.

Opinions please.


Shake n Bake