OP
Member
|
The new Leviton GFI recepts that come in a 3 pack at Home Depot are marked 15a on the box and 20a on the GFI recept. Assume the box is wrong??
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Mar 2001
Posts: 333
Member
|
The receptacle itself is rated for 15A with a 20A feed through rating, unless the receptacle slots are designed to accept a 20A plug.
Steve
|
|
|
|
Joined: Mar 2004
Posts: 55
Member
|
A 15a GFCI is rated for 20a feed though. The rec is only rated at 15a but you can feed a 20a circuit (down range) though that 15a GFCI
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
This is no different than a standard 15 amp duplex receptacle.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Wouldn't you be able to tell from whether or not the nuetral has a horizontal slot on the face?
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Feb 2002
Posts: 840
Member
|
Ryan, good point! There is one difference that Scott did not point out (but I'm sure he knows), a 15 amp receptacle isn't marked "20 amp feed through" like the GFI is.
Peter
|
|
|
|
Joined: Aug 2001
Posts: 545
OP
Member
|
No they don't have the extra slot, but it does say 20 amp on the GFI - not 20 amp feed through.
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Jun 2003
Posts: 681
Member
|
210.21(B)(3) Receptacle Ratings for Various Size Circuits.
this is one of the reasons you have the markings on the GFCIs that are in question.
Pierre
Pierre Belarge
|
|
|
|
Joined: Nov 2003
Posts: 269
Member
|
If it doesn't have the horizontal slot, it is not a 5-20R (20A) receptacle.
John
|
|
|
|
Joined: Aug 2001
Posts: 545
OP
Member
|
Having the slot I believe means a 20a ckt and used as a dedicated circuit. These GFI's do not have the slot, but are marked 20 amp.
The Golden Rule - "The man with the gold makes the rule"
|
|
|
Posts: 75
Joined: June 2012
|
|
|
|
|