Posted By: aldav53 GFI 15 or 20a - 04/08/04 06:18 AM
The new Leviton GFI recepts that come in a 3 pack at Home Depot are marked 15a on the box and 20a on the GFI recept. Assume the box is wrong??
Posted By: stamcon Re: GFI 15 or 20a - 04/08/04 06:38 AM
The receptacle itself is rated for 15A with a 20A feed through rating, unless the receptacle slots are designed to accept a 20A plug.
Posted By: eswets Re: GFI 15 or 20a - 04/08/04 06:40 AM
A 15a GFCI is rated for 20a feed though. The rec is only rated at 15a but you can feed a 20a circuit (down range) though that 15a GFCI
Posted By: Electricmanscott Re: GFI 15 or 20a - 04/08/04 01:26 PM
This is no different than a standard 15 amp duplex receptacle.
Posted By: Ryan_J Re: GFI 15 or 20a - 04/08/04 01:28 PM
Wouldn't you be able to tell from whether or not the nuetral has a horizontal slot on the face?
Posted By: CTwireman Re: GFI 15 or 20a - 04/08/04 07:53 PM
Ryan, good point! [Linked Image]

There is one difference that Scott did not point out (but I'm sure he knows), a 15 amp receptacle isn't marked "20 amp feed through" like the GFI is.
Posted By: aldav53 Re: GFI 15 or 20a - 04/09/04 05:36 AM
No they don't have the extra slot, but it does say 20 amp on the GFI - not 20 amp feed through.
Posted By: PCBelarge Re: GFI 15 or 20a - 04/10/04 02:31 AM
210.21(B)(3) Receptacle Ratings for Various Size Circuits.

this is one of the reasons you have the markings on the GFCIs that are in question.

Pierre
Posted By: electricman2 Re: GFI 15 or 20a - 04/10/04 11:20 PM
If it doesn't have the horizontal slot, it is not a 5-20R (20A) receptacle. [Linked Image]
Posted By: aldav53 Re: GFI 15 or 20a - 04/11/04 04:46 AM
Having the slot I believe means a 20a ckt and used as a dedicated circuit.
These GFI's do not have the slot, but are marked 20 amp.