1 members (Scott35), 534 guests, and 47 robots.
#134967 12/11/02 02:11 AM
Trumpy Offline OP
Paul has a topic on Alternative Energy,
May I post a side-line to this?.
What are the requirements for connecting an
AC Generator to an installation, where you live, where it is not required to give No-Break continuity.
Your thoughts, please-
#134968 12/12/02 03:33 PM
The main requirement is that the generator feeds through a proper transfer switch, switching all phases across, or by other suitable interlocked switches so that there is no possibility of connecting the generator directly to the utility line.
I don't have the specs at hand, but there are certain minimum contact spacing requirements for such switches. and they need to have a center "off" position.
#134969 12/15/02 12:32 AM
Trumpy Offline OP
Paul,
Seemingly, if there is a chance that this type of equipment can back-feed into the
Grid system, does it need to be synchronised with the same?. [Linked Image]
#134970 12/15/02 07:31 AM
No. The rules are based upon making sure that the generator can't back feed into the network, so there's no requirement for synchronization.