Posted By: Trumpy Generators - 12/11/02 06:11 AM
Paul has a topic on Alternative Energy,
May I post a side-line to this?.
What are the requirements for connecting an
AC Generator to an installation, where you live, where it is not required to give No-Break continuity.
Your thoughts, please-
Posted By: pauluk Re: Generators - 12/12/02 07:33 PM
The main requirement is that the generator feeds through a proper transfer switch, switching all phases across, or by other suitable interlocked switches so that there is no possibility of connecting the generator directly to the utility line.

I don't have the specs at hand, but there are certain minimum contact spacing requirements for such switches. and they need to have a center "off" position.
Posted By: Trumpy Re: Generators - 12/15/02 04:32 AM
Paul,
Seemingly, if there is a chance that this type of equipment can back-feed into the
Grid system, does it need to be synchronised with the same?. [Linked Image]
Posted By: pauluk Re: Generators - 12/15/02 11:31 AM
No. The rules are based upon making sure that the generator can't back feed into the network, so there's no requirement for synchronization.