#134967 12/11/02 02:11 AM
Joined: Jul 2002
Posts: 8,450
Likes: 4
Trumpy Offline OP
Member
Paul has a topic on Alternative Energy,
May I post a side-line to this?.
What are the requirements for connecting an
AC Generator to an installation, where you live, where it is not required to give No-Break continuity.
Your thoughts, please-

Wire Pulling Tools for Electricians

Wire Pulling Tools for Electricians, Installers & Maintenance Technicians

#134968 12/12/02 03:33 PM
Joined: Aug 2001
Posts: 7,520
P
Member
The main requirement is that the generator feeds through a proper transfer switch, switching all phases across, or by other suitable interlocked switches so that there is no possibility of connecting the generator directly to the utility line.

I don't have the specs at hand, but there are certain minimum contact spacing requirements for such switches. and they need to have a center "off" position.

#134969 12/15/02 12:32 AM
Joined: Jul 2002
Posts: 8,450
Likes: 4
Trumpy Offline OP
Member
Paul,
Seemingly, if there is a chance that this type of equipment can back-feed into the
Grid system, does it need to be synchronised with the same?. [Linked Image]

#134970 12/15/02 07:31 AM
Joined: Aug 2001
Posts: 7,520
P
Member
No. The rules are based upon making sure that the generator can't back feed into the network, so there's no requirement for synchronization.