Paul has a topic on Alternative Energy, May I post a side-line to this?. What are the requirements for connecting an AC Generator to an installation, where you live, where it is not required to give No-Break continuity. Your thoughts, please-
|
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
The main requirement is that the generator feeds through a proper transfer switch, switching all phases across, or by other suitable interlocked switches so that there is no possibility of connecting the generator directly to the utility line.
I don't have the specs at hand, but there are certain minimum contact spacing requirements for such switches. and they need to have a center "off" position.
|
|
|
|
|
Joined: Jul 2002
Posts: 8,450 Likes: 4
OP
Member
|
Paul, Seemingly, if there is a chance that this type of equipment can back-feed into the Grid system, does it need to be synchronised with the same?. ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
|
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
No. The rules are based upon making sure that the generator can't back feed into the network, so there's no requirement for synchronization.
|
|
|