Hi Rick, A two wire traveler, according to 404.2(a) exception is not required to have a grounded conductor ran in the same cable. I would reject the installation for grabbing another neutral from a different cicuit or require a double trip device to kill the power from the other circuit as required under 210.4(c) exception #2