Rick,
300.3(B)(3) is the specific permission. With nonmetallic raceways or cables all of the circuit conductors are not required to be in the same raceway or cable as long as 300.20 is complied with for metallic boxes. There are no metallic boxes in this installation so there is no violation.
Don


Don(resqcapt19)