Pauluk, a million thanks.
So...in the case of the DC battery showing 12.8 volts, can I assume that the battery is capable of providing up to 31.5 amps? I=E/R = 12.8/.4 = 31.5 amps.
Maybe the voltage will drop and change all the numbers as the amp load is applied. Do I work from the full, unladen voltage to calculate amps and ohms, or do I have to let the amp load bring the voltage down before I'll have good numbers to work with?
"The voltage being lost across the internal resistance of the battery is therefore
12.6 - 11.8 = 0.8V
You know that 2A is flowing through the battery, so the internal resistance by Ohm's Law is then
R = E / I = 0.8 / 2 = 0.4 ohm."
So it looks like you're saying that we're not working off the full EMF when we calculate the resistance through a battery, but instead, we work off the voltage drop and the full amp reading. Seems like the formula would be this:
R=EMF lost/I
It would be easy to make the mistake of working off the full voltage divided by the amps drawn, which would be 11.8 volts/2 amps = 5.9 ohms.
Please correct me if I'm wrong on any of this, I appreciate it.
[This message has been edited by Spark Master Flash (edited 08-03-2003).]