Just to add, I think a wye primary is a poor choice. If the impact protection shorted to ground, and a phase was also faulted to ground on the LV, this would create a neutral shift in the vector. The other phases would go over 230 volts damaging what ever is connected to them.

Just some friendly advice for Norwegian utilities... I mean no harm smile