Around here I would say 99%+ GEC's are terminated in the meter can. So much easier that way.
John
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
MY QUESTION.. what difference does it make? Meter or first ocpd?
The ground is the most unlikely of all conductors to get abused. Once installed it is virtually untouched for it's entire life.
I have yet to get a call or be sent on a call to fix or replace a damaged or a loose ground wire. I am not saying it can't happen. But a Jumbo jet could slam into it too.
This is probably the toughest conductor of them all. As a matter of fact if I am correct a #4 or larger doesnt even require protection or support.
A solid conductor is hard to secure but if done right I see no need to require access. I cant access a buried acorn unless I dig it up...thats not accessible.
-regards
Mustang
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Greg, you and I are in perfect unison here.
Roger
|
|
|
|
Joined: Mar 2004
Posts: 98
Member
|
In our local Power company EUSERC notes, GEC shall be located outside of the sealable section.
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
Roger-I am not trying to beat a dead horse here but I was just curious as to what the concensus was on the subject. I am glad to hear that someone out there is seeing what I am seeing.
I figured a lot of inspectors would reply.
To me it really doesn't matter but it sure is worrysome to try and figure out what each jurisdiction wants. Some places will provide a handbook others it is just time on the pond.
-regards
Greg
|
|
|
|
Joined: Mar 2004
Posts: 16
Member
|
It is my understanding that the GEC must be taken to the first means of disconnect,hence the panel board. 250.24 From that bus you may take it to the meter base. The meter is not a disconnecting means IMO. JG
|
|
|
|
Joined: Mar 2001
Posts: 345
Member
|
In REA coops there was often a service standard requirement to connect the Grounding Electrode Conductor (GEC) to the drip loop at the service drop. It was believed that this would provide superior lightning protection. At one home that I did the heavy up on I ran the GEC from the drip loop through the attic and down to the water service because the basement was finished. The inspector said I couldn't do that and I wrote him a letter to request the decision in writing. He replied with the green sticker in the envelope. I guess that he realized that not having seen it before was not a good reason to turn it down.
It is true that some utilities do not want anyone except their staff to open the meter enclosure. The use of locking rings in place of the lighter gage ceiling rings is becoming more common. Ringless meter enclosures are also being locked rather than sealed with greater frequency now. The connection is allowed inn the an accessible meter enclosure but since utility action can render it inaccessible it may no longer be best practice to terminate it there. -- Tom H
Tom Horne
"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
|
|
|
|
Joined: Jun 2004
Posts: 220
Member
|
JG, 250-24(A)1 doesn't say first to the disconnect, " any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnect." Why would you want to take another wire out to the meter socket when the socket is already bonded to the grounded conductor?
|
|
|