Can a typical RX connector be installed backwards? For example, the section with the two screws inside the panel or box....are there code and or listing violations that would arise?
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
I have used them backwards inside WP boxes so I didnt have to drill an unnecessarily large hole in the siding on which I mounted the box. I will continue to do so.
|
|
|
|
Joined: Nov 2000
Posts: 2,236 Likes: 1
Member
|
What...you don't use WP connectors with WP boxes?
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Redsy,
I like to use a short nipple with ducseal around it that seals when the box is screwed to the siding.
Bill
Bill
|
|
|
|
Joined: Nov 2000
Posts: 2,236 Likes: 1
Member
|
Wait a minute here... I don't have to use WP connectors (at $3.50 each)???
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Originally posted by sparky66wv: What...you don't use WP connectors with WP boxes? When entering the rear of a wall mounted box, I place the box over the hole and caulk around the box.
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
I can't think of a violation that would cover this. I've done the same thing on occaision. I would say that you now have to make a one wire deduction from the number of conductors allowed in that box.
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Anonymous
Unregistered
|
I don't know what it should be a violation. Many boxes have clamps on the inside. Just deduct the appropriate amount from the box fill.
I do see how it might not be weatherproof.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
OP
Member
|
370-16(b)(2) (No allowance shall be required for a clamping mechanism outside the box.) until it's inside...thanks Tom Redsy; I do the same.. Virgil; To your consolation, i do tell customers that there is no such thing as wheatherproof, despite listings, in the northeast. Kinda like kid proof....
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Sparky,
As to your original Question, I would caution to watch for sharp edges at least.
Bill