ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Burning out of return(white) side of 120volt rec
by crselectric. 06/14/19 02:15 AM
Video door bell causing chime activation of coil
by JoeTestingEngr. 06/13/19 12:43 PM
Troubleshooting Voltage Drop Across Relay
by gfretwell. 06/09/19 11:49 AM
Apple Recalls Three-Prong Wall Plug Adapters
by Admin. 06/05/19 09:06 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 5 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Correct Connector #78076
08/14/01 05:46 AM
08/14/01 05:46 AM
S
sparky  Offline OP
Member
Joined: Oct 2000
Posts: 5,372
Can a typical RX connector be installed backwards? For example, the section with the two screws inside the panel or box....are there code and or listing violations that would arise?

2017 / 2014 NEC & Related Books and Study Guides
Re: Correct Connector #78077
08/14/01 07:09 AM
08/14/01 07:09 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I have used them backwards inside WP boxes so I didnt have to drill an unnecessarily large hole in the siding on which I mounted the box. I will continue to do so.

Re: Correct Connector #78078
08/14/01 08:26 AM
08/14/01 08:26 AM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
What...you don't use WP connectors with WP boxes?


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Correct Connector #78079
08/14/01 08:38 AM
08/14/01 08:38 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,905
NY, USA
Redsy,

I like to use a short nipple with ducseal around it that seals when the box is screwed to the siding.

Bill

Re: Correct Connector #78080
08/14/01 10:02 AM
08/14/01 10:02 AM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Wait a minute here...

I don't have to use WP connectors (at $3.50 each)???

[Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Correct Connector #78081
08/14/01 11:48 AM
08/14/01 11:48 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Quote
Originally posted by sparky66wv:
What...you don't use WP connectors with WP boxes?


When entering the rear of a wall mounted box, I place the box over the hole and caulk around the box.

Re: Correct Connector #78082
08/14/01 07:01 PM
08/14/01 07:01 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
I can't think of a violation that would cover this. I've done the same thing on occaision. I would say that you now have to make a one wire deduction from the number of conductors allowed in that box.


Few things are harder to put up with than the annoyance of a good example.
Re: Correct Connector #78083
08/14/01 07:08 PM
08/14/01 07:08 PM
A
Anonymous
Unregistered

I don't know what it should be a violation. Many boxes have clamps on the inside. Just deduct the appropriate amount from the box fill.

I do see how it might not be weatherproof.

Re: Correct Connector #78084
08/14/01 07:12 PM
08/14/01 07:12 PM
S
sparky  Offline OP
Member
Joined: Oct 2000
Posts: 5,372
370-16(b)(2)(No allowance shall be required for a clamping mechanism outside the box.)
until it's inside...

thanks Tom [Linked Image]

Redsy;
I do the same..

Virgil;
To your consolation, i do tell customers that there is no such thing as wheatherproof, despite listings, in the northeast.
Kinda like kid proof....
[Linked Image]

Re: Correct Connector #78085
08/14/01 07:52 PM
08/14/01 07:52 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,905
NY, USA
Sparky,

As to your original Question, I would caution to watch for sharp edges at least.

Bill

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 2
Popular Topics(Views)
255,730 Are you busy
191,696 Re: Forum
181,476 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 15 (0.004s) Memory: 1.0224 MB (Peak: 1.1994 MB) Zlib enabled. Server Time: 2019-06-18 07:38:13 UTC