Burning out of return(white) side of 120volt rec #219879 01/04/19 12:42 AM
Joined: Sep 2006
Posts: 152
C
crselectric Offline OP
Member
I’ve come across a few circuits in Berkeley that have been failing on the return side of 120 volt receptacles? Arcing enough to melt the face of device, in a recent kitchen remodel 2006? All inspected but failing where 1500 watt appliance have been used not old appliances? I believe all were 20amp leviton devices, all new Romex circuits? Possibly just poor workmanship? No loose connections that I’ve found?

Work Gear for Electricians and the Trades
Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #219880 01/04/19 12:59 AM
Joined: Sep 2006
Posts: 152
C
crselectric Offline OP
Member
Was there a bad run of devices in the early 2000s?

Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #219888 01/06/19 05:22 PM
Joined: Apr 2002
Posts: 7,113
HotLine1 Offline
Member
I would lean toward the quality of the terminations (workmanship/talent)

You don't mention if the terminations are on the screw terminals, if it's #12 or #14 NM, or if the devices were 'backstabbed'

We come upon a few burnout receptacles, and IMHO, termination quality is an issue.

I am not aware of any device issues in the early 2000s.

As to your comment on the job being 'inspected', I am not aware of any inspector that has the time, or the authority to remove a device to check terminations. Perhaps there may be some, but none that I know.


John
Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #219900 01/09/19 01:27 AM
Joined: Jul 2004
Posts: 9,394
G
gfretwell Online Content
Member
Are you sure you aren't sharing a neutral on the same ungrounded side of the panel (Miswired multiwire circuit)?

John, I believe an inspector has the "authority" to inspect pretty much everything, time becomes the issue. When I was working travel was my biggest time burner so I looked a a lot of things that surprised people. I was not going to drive 2 hours to look out the window of my truck wink
I have had them pull a device if I saw something funky and if I found something wrong we were going to look at some more. I really had no time constraints tho. It was why I liked my state job and why I never looked for a muni job. I was doing 1, maybe 2 a day. Ten a month was busy for me.


Greg Fretwell
Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #219901 01/09/19 09:15 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
When I do an inspection I start with the thing that's hardest to do in the toughest place to get to.
If they did that right there's a very good chance they did everything else right and my day will be an easy one.
If they screwed it up I know that I'm going to find lots of shortcuts and workarounds in things that are easier.


Ghost307
Re: Burning out of return(white) side of 120volt rec [Re: HotLine1] #219972 02/25/19 03:33 PM
Joined: Sep 2006
Posts: 152
C
crselectric Offline OP
Member
Yes the remodeling contractor did both back stab and screw termination, did not pigtail off, but that goes back to following older installs, the customer said the plug got hot and was arcing at receptacle, Dyson fan heater, 1500 watts

Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #219973 02/26/19 01:29 PM
Joined: Apr 2002
Posts: 7,113
HotLine1 Offline
Member
Yes, a 1500 watt electric heater will find a termination issue. Might take a while, but.....
In an older install, load over time equation, device loses the battle.


John
Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #220011 03/29/19 09:26 PM
Joined: Mar 2004
Posts: 744
B
BigB Offline
Member
The neutral side doesn't get tightened as much as the hot side because most installers are right handed?

Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #220014 04/03/19 12:40 PM
Joined: Dec 2001
Posts: 2,455
T
Texas_Ranger Offline
Member
Oddly enough, 15 years ago an electrician I was working under told me just the same thing, except about junction boxes in 1-ph 2w circuits - it's usually the neutral that burns. I can't say much about that since thankfully I haven't encountered too many loose connections. This was in Europe (Schuko territory, i.e. no polarisation) so left vs. right hand couldn't be an issue. Besides, junction boxes use loose connectors, so no correlation either.

Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #220016 04/04/19 09:50 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
The biggest problem that I come across with overloaded neutrals results from messing up the phases.
If the original installer used a shared neutral it will only carry the maximum load from a single circuit; but if the neutral serves more than 1 phase the neutral can be tasked with carrying twice (or even triple) of the current on a single circuit.

In a home 120/240V:
Shared neutral circuit connected to Black and Red incoming lines.
During renovation the Red ends up being fed from the Black incoming line.
Shared neutral is now being expected to carry twice as much current as intended.
Neither of the hot conductors is overloaded so the circuit breakers never trip.
Neutral carrying twice the rated current overheats, causes fire, house burns down, bad day for everyone involved.

BTW - This has happened enough times (including fatalities) that there is a movement in the NEC to prohibit shared neutrals entirely.


Ghost307
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
258,840 Are you busy
194,361 Re: Forum
183,821 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3