Burning out of return(white) side of 120volt rec #219879
01/04/19 12:42 AM
01/04/19 12:42 AM
C
crselectric  Offline OP
Member
Joined: Sep 2006
Posts: 147
albany, ca
I’ve come across a few circuits in Berkeley that have been failing on the return side of 120 volt receptacles? Arcing enough to melt the face of device, in a recent kitchen remodel 2006? All inspected but failing where 1500 watt appliance have been used not old appliances? I believe all were 20amp leviton devices, all new Romex circuits? Possibly just poor workmanship? No loose connections that I’ve found?

Work Gear for Electricians and the Trades
Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #219880
01/04/19 12:59 AM
01/04/19 12:59 AM
C
crselectric  Offline OP
Member
Joined: Sep 2006
Posts: 147
albany, ca
Was there a bad run of devices in the early 2000s?

Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #219888
01/06/19 05:22 PM
01/06/19 05:22 PM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 7,080
Brick, NJ USA
I would lean toward the quality of the terminations (workmanship/talent)

You don't mention if the terminations are on the screw terminals, if it's #12 or #14 NM, or if the devices were 'backstabbed'

We come upon a few burnout receptacles, and IMHO, termination quality is an issue.

I am not aware of any device issues in the early 2000s.

As to your comment on the job being 'inspected', I am not aware of any inspector that has the time, or the authority to remove a device to check terminations. Perhaps there may be some, but none that I know.


John
Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #219900
01/09/19 01:27 AM
01/09/19 01:27 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,343
Estero,Fl,usa
Are you sure you aren't sharing a neutral on the same ungrounded side of the panel (Miswired multiwire circuit)?

John, I believe an inspector has the "authority" to inspect pretty much everything, time becomes the issue. When I was working travel was my biggest time burner so I looked a a lot of things that surprised people. I was not going to drive 2 hours to look out the window of my truck wink
I have had them pull a device if I saw something funky and if I found something wrong we were going to look at some more. I really had no time constraints tho. It was why I liked my state job and why I never looked for a muni job. I was doing 1, maybe 2 a day. Ten a month was busy for me.


Greg Fretwell
Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #219901
01/09/19 09:15 AM
01/09/19 09:15 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 971
Chicago Illinois USA
When I do an inspection I start with the thing that's hardest to do in the toughest place to get to.
If they did that right there's a very good chance they did everything else right and my day will be an easy one.
If they screwed it up I know that I'm going to find lots of shortcuts and workarounds in things that are easier.


Ghost307
Re: Burning out of return(white) side of 120volt rec [Re: HotLine1] #219972
02/25/19 03:33 PM
02/25/19 03:33 PM
C
crselectric  Offline OP
Member
Joined: Sep 2006
Posts: 147
albany, ca
Yes the remodeling contractor did both back stab and screw termination, did not pigtail off, but that goes back to following older installs, the customer said the plug got hot and was arcing at receptacle, Dyson fan heater, 1500 watts

Re: Burning out of return(white) side of 120volt rec [Re: crselectric] #219973
02/26/19 01:29 PM
02/26/19 01:29 PM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 7,080
Brick, NJ USA
Yes, a 1500 watt electric heater will find a termination issue. Might take a while, but.....
In an older install, load over time equation, device loses the battle.


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,260
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Albert 3
Popular Topics(Views)
253,838 Are you busy
190,301 Re: Forum
179,997 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.003s) Memory: 0.9867 MB (Peak: 1.1435 MB) Zlib enabled. Server Time: 2019-03-18 21:53:46 UTC