ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 1,104 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Mar 2003
Posts: 849
Y
Member
Question
6 - sets of 4 600 MCM copper to service .
By 250.66
Ground wire size to Water Line?

Calculations Please

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: May 2005
Posts: 984
Likes: 2
G
Member
According to the table, anything larger that 1,100 kcmil requires 3/0 Copper (or 250 kcmil Aluminum).
Since you're running parallel sets, you need to run that size ground wire with each set.

Calculations are:
(6) 600 MCM = 3,600 MCM
3,600 MCM > 1,100 MCM


Ghost307
Joined: Mar 2003
Posts: 849
Y
Member
So with the Chart 3/0 is the Size to the water line.

Joined: Mar 2003
Posts: 849
Y
Member
A Ground wire does not go with the Conductors . (only Equipment Grounds go with conductors ,)
This is from the Service Panel to the water line.

Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
I read the chart to say 3/0 is the biggest conductor you ever need and I agree the grounding conductor does not need to be run in each set. They are not usually even going to the same place.


Greg Fretwell
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
The water ground is max 3/0 Cu by NEC, however the design professional may spec something larger. Terminations are at the street side of the water main, and on a compliant sized lug within the main OCP enclosure on the neutral buss.

This conductor does not go with the feeder conductors, as others have said


John

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5