Posted By: Yoopersup Ground wire Size to water Line. - 12/04/17 03:10 PM
Question
6 - sets of 4 600 MCM copper to service .
By 250.66
Ground wire size to Water Line?

Calculations Please
Posted By: ghost307 Re: Ground wire Size to water Line. - 12/04/17 04:43 PM
According to the table, anything larger that 1,100 kcmil requires 3/0 Copper (or 250 kcmil Aluminum).
Since you're running parallel sets, you need to run that size ground wire with each set.

Calculations are:
(6) 600 MCM = 3,600 MCM
3,600 MCM > 1,100 MCM
Posted By: Yoopersup Re: Ground wire Size to water Line. - 12/04/17 05:46 PM
So with the Chart 3/0 is the Size to the water line.
Posted By: Yoopersup Re: Ground wire Size to water Line. - 12/04/17 05:58 PM
A Ground wire does not go with the Conductors . (only Equipment Grounds go with conductors ,)
This is from the Service Panel to the water line.
Posted By: gfretwell Re: Ground wire Size to water Line. - 12/04/17 09:24 PM
I read the chart to say 3/0 is the biggest conductor you ever need and I agree the grounding conductor does not need to be run in each set. They are not usually even going to the same place.
Posted By: HotLine1 Re: Ground wire Size to water Line. - 12/05/17 05:11 PM
The water ground is max 3/0 Cu by NEC, however the design professional may spec something larger. Terminations are at the street side of the water main, and on a compliant sized lug within the main OCP enclosure on the neutral buss.

This conductor does not go with the feeder conductors, as others have said