Question
6 - sets of 4 600 MCM copper to service .
By 250.66
Ground wire size to Water Line?

Calculations Please

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: May 2005
Posts: 984
Likes: 1
G
Member
According to the table, anything larger that 1,100 kcmil requires 3/0 Copper (or 250 kcmil Aluminum).
Since you're running parallel sets, you need to run that size ground wire with each set.

Calculations are:
(6) 600 MCM = 3,600 MCM
3,600 MCM > 1,100 MCM


Ghost307
Joined: Mar 2003
Posts: 849
Y
Member
So with the Chart 3/0 is the Size to the water line.

Joined: Mar 2003
Posts: 849
Y
Member
A Ground wire does not go with the Conductors . (only Equipment Grounds go with conductors ,)
This is from the Service Panel to the water line.

Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
I read the chart to say 3/0 is the biggest conductor you ever need and I agree the grounding conductor does not need to be run in each set. They are not usually even going to the same place.


Greg Fretwell
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
The water ground is max 3/0 Cu by NEC, however the design professional may spec something larger. Terminations are at the street side of the water main, and on a compliant sized lug within the main OCP enclosure on the neutral buss.

This conductor does not go with the feeder conductors, as others have said