Ground wire Size to water Line. #218870
12/04/17 11:10 AM
12/04/17 11:10 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 849
Michigan
Question
6 - sets of 4 600 MCM copper to service .
By 250.66
Ground wire size to Water Line?

Calculations Please

2017 / 2014 NEC & Related Books and Study Guides
Re: Ground wire Size to water Line. [Re: Yoopersup] #218871
12/04/17 12:43 PM
12/04/17 12:43 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 977
Chicago Illinois USA
According to the table, anything larger that 1,100 kcmil requires 3/0 Copper (or 250 kcmil Aluminum).
Since you're running parallel sets, you need to run that size ground wire with each set.

Calculations are:
(6) 600 MCM = 3,600 MCM
3,600 MCM > 1,100 MCM


Ghost307
Re: Ground wire Size to water Line. [Re: Yoopersup] #218872
12/04/17 01:46 PM
12/04/17 01:46 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 849
Michigan
So with the Chart 3/0 is the Size to the water line.

Re: Ground wire Size to water Line. [Re: Yoopersup] #218873
12/04/17 01:58 PM
12/04/17 01:58 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 849
Michigan
A Ground wire does not go with the Conductors . (only Equipment Grounds go with conductors ,)
This is from the Service Panel to the water line.

Re: Ground wire Size to water Line. [Re: Yoopersup] #218874
12/04/17 05:24 PM
12/04/17 05:24 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,348
Estero,Fl,usa
I read the chart to say 3/0 is the biggest conductor you ever need and I agree the grounding conductor does not need to be run in each set. They are not usually even going to the same place.


Greg Fretwell
Re: Ground wire Size to water Line. [Re: Yoopersup] #218879
12/05/17 01:11 PM
12/05/17 01:11 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,084
Brick, NJ USA
The water ground is max 3/0 Cu by NEC, however the design professional may spec something larger. Terminations are at the street side of the water main, and on a compliant sized lug within the main OCP enclosure on the neutral buss.

This conductor does not go with the feeder conductors, as others have said


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,558 Are you busy
190,784 Re: Forum
180,511 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.031s Queries: 15 (0.004s) Memory: 0.9764 MB (Peak: 1.1245 MB) Zlib enabled. Server Time: 2019-04-24 14:13:34 UTC