#218870 - 12/04/17 10:10 AM Ground wire Size to water Line.  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 840
Michigan
Question
6 - sets of 4 600 MCM copper to service .
By 250.66
Ground wire size to Water Line?

Calculations Please


2017 / 2014 NEC & Related Books and Study Guides

#218871 - 12/04/17 11:43 AM Re: Ground wire Size to water Line. [Re: Yoopersup]  
ghost307  Offline
Member
Joined: May 2005
Posts: 919
Chicago Illinois USA
According to the table, anything larger that 1,100 kcmil requires 3/0 Copper (or 250 kcmil Aluminum).
Since you're running parallel sets, you need to run that size ground wire with each set.

Calculations are:
(6) 600 MCM = 3,600 MCM
3,600 MCM > 1,100 MCM


Ghost307

#218872 - 12/04/17 12:46 PM Re: Ground wire Size to water Line. [Re: Yoopersup]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 840
Michigan
So with the Chart 3/0 is the Size to the water line.


#218873 - 12/04/17 12:58 PM Re: Ground wire Size to water Line. [Re: Yoopersup]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 840
Michigan
A Ground wire does not go with the Conductors . (only Equipment Grounds go with conductors ,)
This is from the Service Panel to the water line.


#218874 - 12/04/17 04:24 PM Re: Ground wire Size to water Line. [Re: Yoopersup]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,140
Estero,Fl,usa
I read the chart to say 3/0 is the biggest conductor you ever need and I agree the grounding conductor does not need to be run in each set. They are not usually even going to the same place.


Greg Fretwell

#218879 - 12/05/17 12:11 PM Re: Ground wire Size to water Line. [Re: Yoopersup]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,877
Brick, NJ USA
The water ground is max 3/0 Cu by NEC, however the design professional may spec something larger. Terminations are at the street side of the water main, and on a compliant sized lug within the main OCP enclosure on the neutral buss.

This conductor does not go with the feeder conductors, as others have said


John


Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.002s) Memory: 0.7766 MB (Peak: 0.9247 MB) Zlib enabled. Server Time: 2017-12-11 02:13:31 UTC