Ground wire Size to water Line. #218870 12/04/17 10:10 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
Question
6 - sets of 4 600 MCM copper to service .
By 250.66
Ground wire size to Water Line?

Calculations Please

2017 / 2014 NEC & Related Books and Study Guides
Re: Ground wire Size to water Line. [Re: Yoopersup] #218871 12/04/17 11:43 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
According to the table, anything larger that 1,100 kcmil requires 3/0 Copper (or 250 kcmil Aluminum).
Since you're running parallel sets, you need to run that size ground wire with each set.

Calculations are:
(6) 600 MCM = 3,600 MCM
3,600 MCM > 1,100 MCM


Ghost307
Re: Ground wire Size to water Line. [Re: Yoopersup] #218872 12/04/17 12:46 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
So with the Chart 3/0 is the Size to the water line.

Re: Ground wire Size to water Line. [Re: Yoopersup] #218873 12/04/17 12:58 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
A Ground wire does not go with the Conductors . (only Equipment Grounds go with conductors ,)
This is from the Service Panel to the water line.

Re: Ground wire Size to water Line. [Re: Yoopersup] #218874 12/04/17 04:24 PM
Joined: Jul 2004
Posts: 9,414
G
gfretwell Offline
Member
I read the chart to say 3/0 is the biggest conductor you ever need and I agree the grounding conductor does not need to be run in each set. They are not usually even going to the same place.


Greg Fretwell
Re: Ground wire Size to water Line. [Re: Yoopersup] #218879 12/05/17 12:11 PM
Joined: Apr 2002
Posts: 7,123
HotLine1 Offline
Member
The water ground is max 3/0 Cu by NEC, however the design professional may spec something larger. Terminations are at the street side of the water main, and on a compliant sized lug within the main OCP enclosure on the neutral buss.

This conductor does not go with the feeder conductors, as others have said


John

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 2
andey 2
Popular Topics(Views)
261,321 Are you busy
196,491 Re: Forum
185,747 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3