#190358 11/12/09 08:23 PM
Joined: Oct 2001
Posts: 172
W
Member
Due to the wording in 210.11(C)(3), is it allowable to take a multi wire branch circuit to the bath receptacles and use the other side to power other outlets? To me it seems to be a technical violation of the code as written but not a violation of the intent of this article.

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jan 2005
Posts: 5,485
Likes: 4
Cat Servant
Member
It's the breaker that defines a circuit, not the neutral. That other hot can feed any circuit, anywhere in the house.

Joined: Nov 2007
Posts: 764
K
Member
IMO, it’s allowed, since 210.4,[A] states that "branch circuits recognized in this article [which is Art. 210] shall be permitted as multiwire circuits", then goes on to state "a multiwire circuit shall be permitted to be considered as multiple circuits."Meaning the 12/3 would be two separate circuits, even though the neutral is common to both.

KJay #190364 11/13/09 12:15 AM
Joined: Oct 2001
Posts: 172
W
Member
Thanks KJay thats what I was looking for.