#190358 11/12/09 07:23 PM
Joined: Oct 2001
Posts: 172
W
Member
Due to the wording in 210.11(C)(3), is it allowable to take a multi wire branch circuit to the bath receptacles and use the other side to power other outlets? To me it seems to be a technical violation of the code as written but not a violation of the intent of this article.

Horizontal Ad
Joined: Jan 2005
Posts: 5,476
Likes: 3
Cat Servant
Member
It's the breaker that defines a circuit, not the neutral. That other hot can feed any circuit, anywhere in the house.

Joined: Nov 2007
Posts: 764
K
Member
IMO, it’s allowed, since 210.4,[A] states that "branch circuits recognized in this article [which is Art. 210] shall be permitted as multiwire circuits", then goes on to state "a multiwire circuit shall be permitted to be considered as multiple circuits."Meaning the 12/3 would be two separate circuits, even though the neutral is common to both.

KJay #190364 11/12/09 11:15 PM
Joined: Oct 2001
Posts: 172
W
Member
Thanks KJay thats what I was looking for.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,685
Joined: October 2000
Top Posters(30 Days)
Popular Topics(Views)
333,639 Are you busy
259,012 Re: Forum
240,428 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5