Due to the wording in 210.11(C)(3), is it allowable to take a multi wire branch circuit to the bath receptacles and use the other side to power other outlets? To me it seems to be a technical violation of the code as written but not a violation of the intent of this article.
2017 / 2014 NEC & Related Books and Study Guides
Re: no other outlets [Re: watthead] #190359 11/12/09 08:44 PM
renosteinke Offline
It's the breaker that defines a circuit, not the neutral. That other hot can feed any circuit, anywhere in the house.
Re: no other outlets [Re: watthead] #190360 11/12/09 08:48 PM
K
KJay Offline
IMO, itís allowed, since 210.4,[A] states that "branch circuits recognized in this article [which is Art. 210] shall be permitted as multiwire circuits", then goes on to state "a multiwire circuit shall be permitted to be considered as multiple circuits."Meaning the 12/3 would be two separate circuits, even though the neutral is common to both.
Re: no other outlets [Re: KJay] #190364 11/12/09 11:15 PM
watthead Offline OP
Thanks KJay thats what I was looking for.
2020 National Electrical Code
Code (NEC)
2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman
togol
togol
NW In. USA
Show All Member Profiles
dsk 11
djk 6
Admin 3
263,453 Are you busy
198,526 Re: Forum
187,461 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3