Posted By: watthead no other outlets - 11/13/09 12:23 AM
Due to the wording in 210.11(C)(3), is it allowable to take a multi wire branch circuit to the bath receptacles and use the other side to power other outlets? To me it seems to be a technical violation of the code as written but not a violation of the intent of this article.
Posted By: renosteinke Re: no other outlets - 11/13/09 01:44 AM
It's the breaker that defines a circuit, not the neutral. That other hot can feed any circuit, anywhere in the house.
Posted By: KJay Re: no other outlets - 11/13/09 01:48 AM
IMO, it’s allowed, since 210.4,[A] states that "branch circuits recognized in this article [which is Art. 210] shall be permitted as multiwire circuits", then goes on to state "a multiwire circuit shall be permitted to be considered as multiple circuits."Meaning the 12/3 would be two separate circuits, even though the neutral is common to both.
Posted By: watthead Re: no other outlets - 11/13/09 04:15 AM
Thanks KJay thats what I was looking for.