I took these pictures at my dad's office but we didn't know of these problems until we started remodeling. The picture with the pull-chain light is in a paneled ceiling attached to a single gang box and it turned on when I pulled the string.
The genius that installed the circuits apparently didn’t believe in ground wires because only 6 out of about 60 circuits actually have a ground wire connected to the grounding bus bar. All of the other circuits coming have been grounded through the metal conduit runs.
- Tristan S.
|
|
|
|
Joined: Jul 2007
Posts: 265
Member
|
Is that a three phase panel with a lug missing? Is there an EGC even run into this panel? At least they installed switch duty breakers.
Jimmy
Life is tough, Life is tougher when you are stupid
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
The pull chain lamholder was probablt 'there first'; then the drop ceiling was installed.
Continuous metalic conduit runs do not require a EGC.
John
|
|
|
|
Joined: Aug 2002
Posts: 1,691
Member
|
I love the wire nuts dangling outside the panel!
|
|
|
|
Joined: Nov 2004
Posts: 51
Member
|
37 Breakers and no service Disconect
|
|
|
|
Joined: Oct 2006
Posts: 745
Member
|
Well, it could be a sub panel which is probably the case. That wouldn't require a main disconnect. I'm not crazy about that URD cable being used for the feeders though. No doubt that that "A" phase lug is burned off. Wonder what every third pole space is doing for power?
Is it just me or does it look like that PVC coming in on the upper right has been reduced from 1-1/4" to 1"?
---Ed---
"But the guy at Home Depot said it would work."
|
|
|
|
Joined: Jun 2006
Posts: 110
Member
|
Maybe the burned-out phase is the reason for the "X's" on all those breakers- they don't have one of their legs and thus don't work correctly.
|
|
|
|
Joined: Sep 2002
Posts: 943 Likes: 2
Member
|
It is very unlikely that is a 3 phase panel. That insulator/support is the same on C-H "CH" type single or 3 phase panels.
|
|
|
|
Joined: Jan 2006
Posts: 558
Member
|
I wonder what that piece of NM is feeding at the top of the panel, and I really like the bonding conductor at the bottom exiting from the PVC conduit on the left, not identified as a ground / bond ( Gee I hope no one ever mistakenly connects this conductor to a breaker for whatever reason!) and connected the way it is at the ground buss... Nice! LOL
A.D
|
|
|
|
Joined: Jun 2005
Posts: 821
Member
|
What's with the yellow grounded conductor? I've only seen yellow neutrals in marine-type flexible cable assemblies. And if this isn't a main panel without the benefit of a main disconnect, can someone explain the bond between ground and neutral?
Looks like quite a mess!
|
|
|
|
Joined: Sep 2001
Posts: 806
Member
|
Definitely looks like a 3 phase panel with a missing lug to me.
CH single phase panels use the same insulator and bus support, but the feed lugs are always on the 2 outside positions. Notice the burn marks where the lug used to be...
|
|
|
|
Joined: Sep 2002
Posts: 943 Likes: 2
Member
|
All 1Ø C-H panels I have seen use the center and right side for the lugs, if done that way it uses less copper for the bus stabs.
|
|
|
|
Joined: Mar 2008
Posts: 144
Member
|
The genius that installed the circuits apparently didn’t believe in ground wires because only 6 out of about 60 circuits actually have a ground wire connected to the grounding bus bar. All of the other circuits coming have been grounded through the metal conduit runs.
no wonder why the Panel looks so neat
-Joe “then we'll glue em' then screw em'” -Tom Silva TOH
|
|
|
|
Joined: Sep 2006
Posts: 155
Member
|
looks like quite a pile of dust or ashes? under the missing lug? where is it normal to use yellow for nuetral?
|
|
|
Posts: 264