Office Violations #169655
10/11/07 01:07 AM
10/11/07 01:07 AM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,503
NY, USA
Quote
I took these pictures at my dad's office but we didn't know of these problems until we started remodeling. The picture with the pull-chain light is in a paneled ceiling attached to a single gang box and it turned on when I pulled the string.

The genius that installed the circuits apparently didn’t believe in ground wires because only 6 out of about 60 circuits actually have a ground wire connected to the grounding bus bar. All of the other circuits coming have been grounded through the metal conduit runs.

- Tristan S.

[Linked Image]

[Linked Image]

2017 / 2014 NEC & Related Books and Study Guides
Re: Office Violations [Re: Admin] #169661
10/11/07 07:34 AM
10/11/07 07:34 AM
W
wire_twister  Offline
Member
Joined: Jul 2007
Posts: 265
Georgia USA
Is that a three phase panel with a lug missing? Is there an EGC even run into this panel? At least they installed switch duty breakers.


Jimmy

Life is tough, Life is tougher when you are stupid
Re: Office Violations [Re: wire_twister] #169663
10/11/07 07:40 AM
10/11/07 07:40 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,986
Brick, NJ USA
The pull chain lamholder was probablt 'there first'; then the drop ceiling was installed.

Continuous metalic conduit runs do not require a EGC.



John
Re: Office Violations [Re: HotLine1] #169674
10/11/07 02:33 PM
10/11/07 02:33 PM
S
SvenNYC  Offline
Member
Joined: Aug 2002
Posts: 1,691
New York City
I love the wire nuts dangling outside the panel!

Re: Office Violations [Re: SvenNYC] #169694
10/12/07 11:38 AM
10/12/07 11:38 AM
B
BElder  Offline
Member
Joined: Nov 2004
Posts: 51
Paradise, CA. U.S.A.
37 Breakers and no service Disconect

Re: Office Violations [Re: BElder] #169695
10/12/07 01:10 PM
10/12/07 01:10 PM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
Well, it could be a sub panel which is probably the case. That wouldn't require a main disconnect. I'm not crazy about that URD cable being used for the feeders though. No doubt that that "A" phase lug is burned off. Wonder what every third pole space is doing for power?

Is it just me or does it look like that PVC coming in on the upper right has been reduced from 1-1/4" to 1"?


---Ed---

"But the guy at Home Depot said it would work."
Re: Office Violations [Re: EV607797] #169701
10/12/07 02:35 PM
10/12/07 02:35 PM
T
trobb  Offline
Member
Joined: Jun 2006
Posts: 110
Iowa City, IA
Maybe the burned-out phase is the reason for the "X's" on all those breakers- they don't have one of their legs and thus don't work correctly.

Re: Office Violations [Re: trobb] #169708
10/12/07 09:19 PM
10/12/07 09:19 PM
N
NORCAL  Offline
Member
Joined: Sep 2002
Posts: 880
It is very unlikely that is a 3 phase panel. That insulator/support is the same on C-H "CH" type single or 3 phase panels.

Re: Office Violations [Re: NORCAL] #169726
10/13/07 04:04 PM
10/13/07 04:04 PM
R
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
I wonder what that piece of NM is feeding at the top of the panel, and I really like the bonding conductor at the bottom exiting from the PVC conduit on the left, not identified as a ground / bond ( Gee I hope no one ever mistakenly connects this conductor to a breaker for whatever reason!) and connected the way it is at the ground buss... Nice! LOL

A.D

Re: Office Violations [Re: Rewired] #169738
10/14/07 05:49 AM
10/14/07 05:49 AM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
What's with the yellow grounded conductor? I've only seen yellow neutrals in marine-type flexible cable assemblies. And if this isn't a main panel without the benefit of a main disconnect, can someone explain the bond between ground and neutral?

Looks like quite a mess!


Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 95
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,160 Are you busy
185,635 Re: Forum
174,999 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 16 (0.005s) Memory: 1.0254 MB (Peak: 1.2056 MB) Zlib enabled. Server Time: 2018-07-22 16:16:33 UTC