Quote
I took these pictures at my dad's office but we didn't know of these problems until we started remodeling. The picture with the pull-chain light is in a paneled ceiling attached to a single gang box and it turned on when I pulled the string.

The genius that installed the circuits apparently didn’t believe in ground wires because only 6 out of about 60 circuits actually have a ground wire connected to the grounding bus bar. All of the other circuits coming have been grounded through the metal conduit runs.

- Tristan S.

[Linked Image]

[Linked Image]

Insulated Tools for Electricians

Insulated Tools for Electricians, Installers & Maintenance Technicians

Admin #169661 10/11/07 07:34 AM
Joined: Jul 2007
Posts: 264
W
Member
Is that a three phase panel with a lug missing? Is there an EGC even run into this panel? At least they installed switch duty breakers.


Jimmy

Life is tough, Life is tougher when you are stupid
Joined: Apr 2002
Posts: 7,413
Likes: 10
Member
The pull chain lamholder was probablt 'there first'; then the drop ceiling was installed.

Continuous metalic conduit runs do not require a EGC.



John
Joined: Aug 2002
Posts: 1,691
S
Member
I love the wire nuts dangling outside the panel!

Joined: Nov 2004
Posts: 51
B
Member
37 Breakers and no service Disconect

Joined: Oct 2006
Posts: 745
E
Member
Well, it could be a sub panel which is probably the case. That wouldn't require a main disconnect. I'm not crazy about that URD cable being used for the feeders though. No doubt that that "A" phase lug is burned off. Wonder what every third pole space is doing for power?

Is it just me or does it look like that PVC coming in on the upper right has been reduced from 1-1/4" to 1"?


---Ed---

"But the guy at Home Depot said it would work."
Joined: Jun 2006
Posts: 110
T
Member
Maybe the burned-out phase is the reason for the "X's" on all those breakers- they don't have one of their legs and thus don't work correctly.

Insulated Tools for Electricians

Insulated Tools for Electricians, Installers & Maintenance Technicians

trobb #169708 10/12/07 09:19 PM
Joined: Sep 2002
Posts: 947
Likes: 4
N
Member
It is very unlikely that is a 3 phase panel. That insulator/support is the same on C-H "CH" type single or 3 phase panels.

Joined: Jan 2006
Posts: 558
R
Member
I wonder what that piece of NM is feeding at the top of the panel, and I really like the bonding conductor at the bottom exiting from the PVC conduit on the left, not identified as a ground / bond ( Gee I hope no one ever mistakenly connects this conductor to a breaker for whatever reason!) and connected the way it is at the ground buss... Nice! LOL

A.D

Joined: Jun 2005
Posts: 821
S
Member
What's with the yellow grounded conductor? I've only seen yellow neutrals in marine-type flexible cable assemblies. And if this isn't a main panel without the benefit of a main disconnect, can someone explain the bond between ground and neutral?

Looks like quite a mess!