I don't know any of the history behind this, but thought it would make a good addition to the board. -- tg
|
|
|
|
Joined: Jun 2003
Posts: 1,143
Member
|
Well, completely ignoring the "Non Metallic Cable in Free Air" to the right of the Panel, how about flagging the lovely multi colored (other than white, white identified, or bare copper / Aluminum) going to the "neutral" / Grounded buss?
|
|
|
|
Joined: Aug 2002
Posts: 1,081
Member
|
Interesting how some of the NM sheathing is inside the panel, and some is cut way too short. how about flagging the lovely multi colored... Patriotism. Speaking of flagging, June 14th is Flag Day. Here's the real punchline: My wife took this picture. Really!
|
|
|
|
Joined: Feb 2004
Posts: 1,438
Member
|
Thinkgood... Good to hear your wife is keeping an eye out for forum material But this looks like its in someones basement, a friend of a friend of a friend? ... I wonder if the "thrifty nickel" guys who did an installation I came across moved! Shame for that QO panel to be treated this way! -Randy
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
Shame for that QO panel to be treated this way! Definitely -- All that lovely wide-open space. (Those who have seen the pics of British panels know what I mean.... )
|
|
|
|
Joined: Aug 2002
Posts: 1,081
Member
|
a friend of a friend of a friend? House hunting!
|
|
|
|
Joined: Feb 2002
Posts: 183
Member
|
Looks like a work in progress. Seems that someone is adding some new circuits - the hanging yellow romex. There's an open KO in the top of the panel, hopefully for those new ones.
It looks like there are neutrals and grounds mixed on the right bus; I can't see the bonding screw so I am not sure if this is a subpanel or not, but that lone ground coming in thru the conduit on the upper right implies that this is the main. The white reidentified with green as a ground looks a little to small to be restriped green.
Blues are OK for neutral (harmonized wiring uses blue for that) but having blue for both hot and neutral can be confusing. /mike
|
|
|
|
Joined: Feb 2002
Posts: 840
Member
|
n1ist,
Blue is not OK for use as a neutral. IMO, The blue neutral from the "harmonized" system is a code violation. See article 200.
White cannot be reidentified as green no matter what the size. White may only be reidentified for use as an ungrounded conductor as part of a cable assembly.
Peter
Peter
|
|
|
|
Joined: Dec 2001
Posts: 2,498
Member
|
I also like the way the yellow NM is run to the bottom right breaker. Guess they didn't try to put on the panel cover so far
|
|
|
|
Joined: Jun 2003
Posts: 1,143
Member
|
At least it's yellow NM, and not the yellow extension cord seen elsewhere in these pages!
|
|
|
Posts: 28
Joined: May 2007
|
|
|
|