Quote
So, then it doesn't apply to the disposal and dishwasher. Mysteriously its not necessary to have those on a GFI...

There is no mystery.

210.8(A)(6) requires outlets that serve a kitchen countertop to be GFCI protected.

210.52(B)(3) requires the two appliance circuits on a countertop.

210.52(C)(5) allows the DW/Disp receptacle outlets to be excluded from 210.8(A)(6), because they are not required by 210.52(B)(3).


~~ CELTIC ~~