I should have included the USE info too.

2003 UL White Book
SERVICE CABLE (TXKT)
SERVICE ENTRANCE CABLE (TYLZ)
GENERAL

Quote
Types USE and USE-2 — Indicates cable for underground installation including direct burial in the earth. Cable in sizes 4/0 AWG and smaller and having all conductors insulated is suitable for all of the underground uses for which Type UF cable is permitted by the NEC. Types USE and USE-2 are not suitable for use in premises or aboveground except to terminate at the service equipment or metering equipment. Both the insulation and the outer covering, when used, on single and multiconductor Types USE and USE-2, are suitable for use where exposed to sun.


Bob Badger
Construction & Maintenance Electrician
Massachusetts