Tom do you have any references for using SE underground?
2003 UL White Book SERVICE CABLE (TXKT) SERVICE ENTRANCE CABLE (TYLZ) GENERAL
Quote
The cable is designated as follows: Type SE — Indicates cable for aboveground installation. Both the individual insulated conductors and the outer jacket or finish of Type SE are suitable for use where exposed to sun.
I can not find anything that says Type SE is allowed underground.
Bob
Bob Badger Construction & Maintenance Electrician Massachusetts