Guys,
It appears that I'm wrong on this issue. CMP5 addressed this in the '99ROC. It is still not completely clear as I don't think that the "green" screws are listed devices for grounding and if they are not, then the only choice would be the push-on grounding clip.
5- 42 - (250-8): Reject
SUBMITTER: Don Ganiere, Ottawa, IL
COMMENT ON PROPOSAL NO: 5-71
RECOMMENDATION: The proposal should be accepted in principle. Add new text: " Machine screws and bolts shall be permitted to secure listed pressure connectors and solid conductors ".
SUBSTANTIATION: Machine screws and bolts are used to secure pressure connectors and solid connectors. A machine screw is not a listed means and use of machine screws would be a violation. New wording should be added: "Machine screws and bolts shall be
permitted to secure listed pressure connectors and solid conductors".
PANEL ACTION: Reject.
PANEL STATEMENT: The use of a machine screw to secure a listed pressure connector must be installed in accordance with the
manufacturers. instruction. Section 110-14(a) does not permit the connection of a solid conductor with an ordinary machine screw.
NUMBER OF PANEL MEMBERS ELIGIBLE TO VOTE: 16
VOTE ON PANEL ACTION:
AFFIRMATIVE: 14
NEGATIVE: 2
EXPLANATION OF NEGATIVE:
DOBROWSKY: The comment should be accepted in principle and the proposed additional text revised as follows: "Machine screws identified for the purpose shall be permitted to secure 10 AWG or smaller conductors." This concept is permitted as described in Section 110.14(A). Forming a loop in a 14 AWG through 10 AWG solid conductor and securing it with a screw in compliance with Section 110.14(A) should be acceptable in Section 250.8.
HAMMEL: The comment should be accepted in principle and the proposed additional text revised as follows: "Machine screws identified for the purpose shall be permitted to secure 10AWG or smaller conductors." This concept is permitted as described in Section 110.14(A).
Forming a loop in a 14AWG through 10AWG solid conductor and securing it with a screw in compliance with Section 110.14(A) should be acceptable in Section 250.8.
___________________
Don