There is no code rule that requires the use of a "green" screw for the connection of the EGC. The use of the clamp screw with the clamp still installed would be a violation of 250.148(A), but there is no violation if the clamp is removed and the clamp screw is used to connect the EGC.
Don


Don(resqcapt19)