Bill,

The problem of a ground-fault taking out the supply to everything is probably the biggest drawback of the whole-house ELCB.
Some new systems are now using a "split-load consumer unit" with the RCD/GFI protecting most circuits but pre-GFI circuits for lights, and sometimes for things such as fridgs and freezers.

Obviously where a GFI is required for all circuits (i.e. most buildings with their own ground rod) the only way to implement a split-load system is to use two separate GFIs. Easy enough to install, but not cheap.

The biggest problem with stray ground currents was/is with the older voltage-type ELCB and parallel earth paths desensitizing the device. For example, the water pipes in the house would be conneced to the house ground wiring, so it was important to install the ground rod far enough away that its ground resistance gradient didn't overlap with that of any buried water service pipe.

Another problem where houses are close (quite common in our relatively crowded land) is that a ground fault on one house could trip the ELCB on a neighboring house if the two ground rods were too close.

Fortunately, these problems are gradually disappearing as the older type ELCBs are taken out of service.