KJay, I disagree, this is not a violation of NEC 110.3. The method of ground fault, overload or overcurrent detection at any point upstream has no bearing on the listing. A GFCI receptacle is no different than ground fault detection on a switchboard, or the ground fault detection integrated into an AFCI breaker, both of which are unquestionably acceptable to feed a GFCI receptacle.