I've never been involved with delta systems, so perhaps my figuring is way off base, but I'm with Radar.

The way I see it, although there is a basic 120-degree difference between phase currents, the A-C winding with its center-tap neutral is introducing another factor to the overall picture.

Whenever you have a tapped transformer winding, if you use that tap as your reference point, then the voltages at each end will be 180 degrees out of phase with each other.
Let's build up a system:

Start with just a single center-tapped winding, like a 3-wire 1120/240V service, and let's still call the hot legs A and C. We know that the neutral current will be the difference between A and C. Now add one extra winding from A to provide a B-phase in the form of an open delta, but don't connect any load to that phase. Obviously there can be no current in that winding, so the neutral current will remain unchanged.

Now add a third winding B-to-C to close the delta, but still leave no load on the B-phase. Will the neutral current change then? I don't think so, because the basic voltage/current relationships between the phases are still the same. There will be very little (in a theoretically perfect arrangement zero) current flowing in the A-B and B-C windings, will there not? So the A-C winding is still acting just like a 3-wire 120/240V service.

Now add a 3-ph delta-connected load to A-B-C. Obviously there will now be current flowing in all three windings, but will that affect the neutral?

I do not believe so, since the 3-ph load has no neutral connection. The current in the A-C winding will increase, but as the voltages on the A and C phases have not changed with respect to neutral/ground, the single-phase loads connected A-N and C-N are still drawing the same amount of current, and thus the neutral will still carry just the difference of the single-phase loads on A and C.