OK - here's my initial cut at this. Start with the 3Ø component - take 240,000 VA (80,000 VA per phase) divided by 240 * SqRt of 3, which comes out to around 578 amps.
Next I'd ignore the ØA load as it just counteracts the ØC load. The ØC load is 41,000 - divide that by 120V for another 342 amps (on the C leg).
All in all, 578 + 342 = 920 Amps <-- highest leg (which is ØC).
Taking 920 amps X 1.25 = 1,150 amps, I'd vote for a 1,200 amp OCP.
Tomorrow at work I'll plug the raw data into a panel schedule and see what it says.
Radar
[This message has been edited by Radar (edited 02-09-2006).]
There are 10 types of people. Those who know binary, and those who don't.