The way I figured this is as follows:
<OL TYPE=1>
[*] 3 Phase Load = 192.70 Amps (80 KVA),
[*] 1 Phase "240 Volt" Load = 141.67 Amps (34 KVA),
[*] 1 Phase "120 Volt" Load = 58.34 Amps (7 KVA).
</OL>
Nominal Totals Per Line ("Phase"):
<OL TYPE=A>
[*] Line "A": 334.37 Amps (80 KVA @ 240v 3Ø + 34 KVA @ 240v),
[*] Line "B": 192.70 Amps (80 KVA @ 240v 3Ø),
[*] Line "C": 392.71 Amps (80 KVA @ 240v 3Ø + 34 KVA @ 240v + 7 KVA @ 120v).
</OL>
Panelboard + Feeder Size
Nominal Load Values WITH LCL:
* Panelboard: 600 Amps - 240/120V 3Ø 4 Wire
* Feeder: 1,000 MCM THHN/THWN Cu. (or equivalent Parallel Feeders, protected by 500 Amp 3 Pole OCPD).
Nominal Load Values WITHOUT LCL:
* Panelboard: 400 Amps - 240/120v 3Ø 4 Wire
* Feeder: 600 MCM THHN/THWN Cu. (or equivalent Parallel Feeders, protected by 400 Amp 3 Pole OCPD).
BTW: Load on the Grounded (Neutral) Conductor would be 7 KVA (58.34 Amps)
Scott35