And the horror show continues... this thing gives me the creeps every time I see it..and now, it appears that the cutouts are right by the door!!

So changing a fuse or closing in or opening those cutouts effectively forces you to be isolated inside the room?? And the close spacing makes a phase-to-phase flashover a distinct possibility, especially since they're not outdoors in open air.

Speaking of which, is there any ventilation to the outside of the building? I don't see any vents of any kind (and if there were the room wouldn't have been in total darkness when you arrived.)

Rabbit, please tell me I'm wrong......this whole thing has some seriously unsafe design issues!!

edited to add:

I also wonder if the POCO is aware of this situation? And if they don't care, heads should roll!!!