#97066 - 01/19/06 07:30 PM Office receptacle placement  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
I am assuming the 12' rule of the receptacle placement also applies to a commercial office.
And the # of receptacles on a 20A circuit also applies to a commercial office?
Or both of the above are only for a residential setting?

Thank you
Edward


Thanks
Edward

2017 / 2014 NEC & Related Books and Study Guides

#97067 - 01/19/06 08:02 PM Re: Office receptacle placement  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
You don't need any receptacles in an office.

Each receptacle in a commercial building counts as 180 VA.

There is no limit to the amount of receptacles on a circuit in a dwelling.


Ryan Jackson,
Salt Lake City

#97068 - 01/19/06 09:30 PM Re: Office receptacle placement  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
Thanks Ryan.

So in an office situation there is a limit on #of receptacle per circuit.

Edward


Thanks
Edward

#97069 - 01/19/06 09:31 PM Re: Office receptacle placement  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
Doesn't office count as commercial space???

Thanks
Edward


Thanks
Edward

#97070 - 01/20/06 08:52 AM Re: Office receptacle placement  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Yes, an office is a commercial space, therefore the 180VA rule of 220.14 applies.

For example, how many receptacles can be on a 20 ampere branch circuit?
20A*120V=2400VA
2400/180=13 devices on a 20 ampere circuit.


Ryan Jackson,
Salt Lake City

#97071 - 01/20/06 09:57 AM Re: Office receptacle placement  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
Thanks Ryan


Thanks
Edward

#97072 - 01/21/06 12:49 PM Re: Office receptacle placement  
XtheEdgeX  Offline
Member
Joined: Apr 2005
Posts: 116
Florida
I thought the spacing was 6', and not 12'.
210.52(A)(1) States the spacing to be 6' instead of 12'. Correct me if I'm wrong.


#97073 - 01/21/06 01:11 PM Re: Office receptacle placement  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
The rule requires that no point on the floor be more than 6' from a receptacle.

If you place the outlets every 12' than no point along the floor line will be further than 6' from at least one receptacle.

Quote
210.52(A)(1) Spacing. Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 1.8 m (6 ft) from a receptacle outlet.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#97074 - 01/21/06 01:40 PM Re: Office receptacle placement  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
To be clear for everyone reading this thead, the rules in 210.52 only apply to dwelling units. There are no receptacle spacing rules for other occupancies.
Don


Don(resqcapt19)

#97075 - 01/21/06 04:26 PM Re: Office receptacle placement  
XtheEdgeX  Offline
Member
Joined: Apr 2005
Posts: 116
Florida
OK, I've not been required to do much in the residential area, so I feel kind of dumb here. So what you're saying is, I can measure any place on a floor, any where in the room, and it should be no more than 6' from a receptacle, OR, is it measured any where along the line at the bottom of the wall, even if you measure from one wall across a corner to another wall, should be no more than 6'?


Page 1 of 3 1 2 3

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.002s) Memory: 0.8177 MB (Peak: 0.9942 MB) Zlib enabled. Server Time: 2017-12-15 06:32:47 UTC