Office receptacle placement #97066 01/19/06 08:30 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
I am assuming the 12' rule of the receptacle placement also applies to a commercial office.
And the # of receptacles on a 20A circuit also applies to a commercial office?
Or both of the above are only for a residential setting?

Thank you
Edward


Thanks
Edward
2017 / 2014 NEC & Related Books and Study Guides
Re: Office receptacle placement #97067 01/19/06 09:02 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
You don't need any receptacles in an office.

Each receptacle in a commercial building counts as 180 VA.

There is no limit to the amount of receptacles on a circuit in a dwelling.


Ryan Jackson,
Salt Lake City
Re: Office receptacle placement #97068 01/19/06 10:30 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
Thanks Ryan.

So in an office situation there is a limit on #of receptacle per circuit.

Edward


Thanks
Edward
Re: Office receptacle placement #97069 01/19/06 10:31 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
Doesn't office count as commercial space???

Thanks
Edward


Thanks
Edward
Re: Office receptacle placement #97070 01/20/06 09:52 AM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
Yes, an office is a commercial space, therefore the 180VA rule of 220.14 applies.

For example, how many receptacles can be on a 20 ampere branch circuit?
20A*120V=2400VA
2400/180=13 devices on a 20 ampere circuit.


Ryan Jackson,
Salt Lake City
Re: Office receptacle placement #97071 01/20/06 10:57 AM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
Thanks Ryan


Thanks
Edward
Re: Office receptacle placement #97072 01/21/06 01:49 PM
Joined: Apr 2005
Posts: 116
X
XtheEdgeX Offline
Member
I thought the spacing was 6', and not 12'.
210.52(A)(1) States the spacing to be 6' instead of 12'. Correct me if I'm wrong.

Re: Office receptacle placement #97073 01/21/06 02:11 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
The rule requires that no point on the floor be more than 6' from a receptacle.

If you place the outlets every 12' than no point along the floor line will be further than 6' from at least one receptacle.

Quote
210.52(A)(1) Spacing. Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 1.8 m (6 ft) from a receptacle outlet.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Office receptacle placement #97074 01/21/06 02:40 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
To be clear for everyone reading this thead, the rules in 210.52 only apply to dwelling units. There are no receptacle spacing rules for other occupancies.
Don


Don(resqcapt19)
Re: Office receptacle placement #97075 01/21/06 05:26 PM
Joined: Apr 2005
Posts: 116
X
XtheEdgeX Offline
Member
OK, I've not been required to do much in the residential area, so I feel kind of dumb here. So what you're saying is, I can measure any place on a floor, any where in the room, and it should be no more than 6' from a receptacle, OR, is it measured any where along the line at the bottom of the wall, even if you measure from one wall across a corner to another wall, should be no more than 6'?

Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 10
Trumpy 7
Popular Topics(Views)
279,176 Are you busy
212,237 Re: Forum
199,252 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3