A restaurant has a 30 foot long line of booths in the middle of their floor space. The walls at the end of the row are tiled in marble. There is an existing outlet on one end and they want to place a lamp om the opposite wall. They want me to install a 35 foot long cord on the lamp so that thet can run the cord underneath the booths and plug it into the outlet. I pulled up some cushions and there is plenty of free space, safe from physical damage, near the floor. Is there any NEC violation here?
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
400.8 Uses Not Permitted. Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
(1)As a substitute for the fixed wiring of a structure
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Mar 2002
Posts: 582
Member
|
Bob, I would normally agree with your code quote, but I was thinking ..... Since there is no requirement to provide receptacles in the restaurant, who is to say that the flexible cord is acting as a substitute for the fixed wiring of a structure. Thinking about it another way, if a 6' cord was installed on a lamp to reach a receptacle, using the logic in your response, wouldn't that also be considered as a substitute for the fixed wiring of a structure? A receptacle could be installed at the lamp! I don't know the answer, I'm just being critical. I've never found a limit to a cord length written anywhere (except 645 for IT equipment)
Ron
|
|
|
|
Joined: Jun 2005
Posts: 91
Member
|
You can build a lamp with a 35' cord, I don't see a prohibition there. I'd say hiding it under booth seats is concealing the cord in the finish of the building, and is also exposing it to damage. That may sound a bit nutty, let me explain. The freshly built fast food joints are looking to devote as much space to tables as possible, and reduce the amount of kitchen/office/cooler space as much as they can, to maximize the use of a new building. It is becoming more common to store files in the seats in the dining room to make use of the otherwise unused space. It's not as though you'll pull up a seat and find filled out W-4 forms and P&L statements under there, but you could find promotional material, outdated POP material, training materials, uniforms, etc out there. Space behind that counter is at a premium, and whatever doesn't have to be, isn't. I am not making this up. Dropping boxes of paperwork and old displays into that space makes it exposed to physical damage.
-George
|
|
|
|
Joined: Jun 2005
Posts: 91
Member
|
(And yes, it does make it a bit awkward when you hire a new employee and have to wait for people to leave the booth so you can get the guy a uniform.)
-George
|
|
|
|
Joined: Feb 2002
Posts: 375
Member
|
elecbob ---
I don't think it is a code violation.
Your local inspector may think it is.
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
I'm with iwire (Bob) on this. Although it is a cord connected item, like many other cord-connected items, running the cord though building finish makes it premisis wiring, and a code violation. Why not run, a new receptical in MC, or AC from that outlet to the location accessibe under the nearest cushion?
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Aug 2002
Posts: 141
OP
Member
|
Presently, the lamp cord is tucked in between the wall and the back cushion. It exits underneath the bottom cushion and is plugged into an extension cord which the fire department does not like. The extension cord exits at the other end through a gap at the end of the kick space board and is plugged into an outlet there. Are the removable bottom cushion considered a "building finish"? BTW: It's easy to drop $75 for a dinner in this place.
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
High end restaurateur seeking low end pricing.
I just looked at a job for a small electric sign at a bank. They don't want a permit, but want to know if I'd do it anyway. The last "electrician" hired to install holiday light strands on about 8 trees for year-round use, pulled power from the site light posts. He attached a wp box to the pole base and spliced SJTW extension cords inside it. Then he buried the cord a few inches in the ground to get to the trees. Up the trees with the extension cord to a 4-way "cube-tap" to pug in the light strands. At one point, the cord even goes under a concrete walkway. All of this is in a nice suburban area with pedestrian traffic. (Of course no GFCIs) Since the holiday lights have all burned out, they also want to know if I'd like to replace them.
No & no.
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
OK, 1 more opinion... Cord cannot be used as a permanent wiring method. 400-8 & 400-7 approved and non approved uses for cord
Also, an extension cord (pluged into the lamp cord) is a no-no. The FD should frown upon this, as we all do.
Redsy; I've seen the same type of decorative lighting install. 14 gauge SO/SJ;
John