Liquidtight to Schedule 40/80 #95866
10/15/05 09:14 AM
10/15/05 09:14 AM
InspectorE  Offline OP
Joined: Oct 2004
Posts: 51
Hudson WI USA
Is there any code compliant method of connecting from schedule 40/80 to liquidtight conduit? I'm not looking for a single "tweenie" connector, use of a junction box would be fine. An insulated grounding conductor would be run the full length.

2017 / 2014 NEC & Related Books and Study Guides
Re: Liquidtight to Schedule 40/80 #95867
10/15/05 11:12 AM
10/15/05 11:12 AM
Tom  Offline
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Presuming that your schedule 40 or 80 is RNMC, you could glue a female adapter on the end, screw in the connector for the flex & carry on.


Few things are harder to put up with than the annoyance of a good example.
Re: Liquidtight to Schedule 40/80 #95868
10/15/05 02:27 PM
10/15/05 02:27 PM
InspectorE  Offline OP
Joined: Oct 2004
Posts: 51
Hudson WI USA
I saw that as a possible combination. However, I wasn't sure that the manufacturer of the liquid tight connector meant for the connector to be used with other than a metal box where a metal locknut would be used on the inside of the box. Since the rubber washer on the liquid tight connector is normally locked tight by the metal lock washer on the inside of the box, I wasn't sure that the same would be true if the connector was made tight into the pvc female connector.

Sounds like it is ok, then.


Re: Liquidtight to Schedule 40/80 #95869
10/15/05 08:52 PM
10/15/05 08:52 PM
HotLine1  Offline

Joined: Apr 2002
Posts: 6,936
Brick, NJ USA
THe sealing ring (rubber washer) should be seated/compressed when the flex conn is wrench tte in the PVC FA.

As to the 'listing', my books are all in the office.


Re: Liquidtight to Schedule 40/80 #95870
10/16/05 11:32 AM
10/16/05 11:32 AM
earlydean  Offline
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
We can never assume that there will never be moisture entering the conduit. PVC conduit leaks quite well. Take the gasket and put it in the junk drawer for the time you'll need it when the manufacturer shorts you.
Arrange the conduit run to drain. Special fittings are made for this purpose. Use a "T" condulet, with the drain at the bottom of the "T".

Re: Liquidtight to Schedule 40/80 #95871
10/18/05 06:12 PM
10/18/05 06:12 PM
boggerbutt2454  Offline
Joined: Feb 2005
Posts: 44
Concord NC USA
Can you use Carflex? Non-metallic seal tight flex.

Re: Liquidtight to Schedule 40/80 #95872
10/18/05 11:56 PM
10/18/05 11:56 PM
Tripp  Offline
Joined: Sep 2005
Posts: 99
I believe that "Carflex" is a brand name, by Carlon, for LFNC (liquidtight flexible nonmetallic conduit).


2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 5
Admin 4
Popular Topics(Views)
244,891 Are you busy
182,004 Re: Forum
172,034 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 14 (0.004s) Memory: 0.9842 MB (Peak: 1.1326 MB) Zlib enabled. Server Time: 2018-03-24 19:25:15 UTC