This is a 200a 1ph. UG residential service.

No metallic water lines,interior or exterior. Meterbase is back to back with a 200a main brkr. panel. Short pvc nipple between them. # 4 solid copper from lug in MB down to 2 ground rods 6' apart.

No Ahj here. Homeowner hired a retired elec inspector to look at job and he says the #4 must come from the panel.

Can anyone give me a code art.for this?

Russell

Horizontal Ad
#88267 05/25/04 05:15 PM
Joined: May 2002
Posts: 1,716
R
Member
Hello Russell, It sounds as though this retired inspector is from an area that is not used to seeing this connection at the meter.

Roger

[This message has been edited by Roger (edited 05-25-2004).]

#88268 05/25/04 05:29 PM
Joined: Nov 2002
Posts: 558
G
Member
Hi Roger.

Thats what I thought. I don't see the difference in this situation.

Russell

#88269 05/25/04 08:18 PM
Joined: Feb 2002
Posts: 840
C
Member
Russell,

The connection to a ground rod doesn't need anything larger than #6 Copper. Nothing wrong with the #4 of course. [Linked Image]

Peter


Peter
#88270 05/25/04 08:47 PM
Joined: Nov 2002
Posts: 558
G
Member
You're right CT. It's just a habit. [Linked Image]

[This message has been edited by ga.sparky56 (edited 05-25-2004).]

#88271 05/27/04 10:13 PM
Joined: Apr 2004
Posts: 60
M
Member
Here in Washington, the meter base is not considered to be accessible to the occupant. Technically, the power company says you need to call and coordinate cutting the seal, there its not really accessible. Therefore, the GEC can not be run from there.

This is a AHJ call, and not an NEC code rule except for a strict interpretation of 250.68 which says the GEC must be accessible.


Mark
Kent, WA

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,443
Joined: July 2002
Top Posters(30 Days)
Popular Topics(Views)
340,084 Are you busy
265,525 Re: Forum
246,539 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5