service disconnects #80365
04/03/02 11:17 PM
04/03/02 11:17 PM
K
kenrod3020  Offline OP
Member
Joined: Feb 2002
Posts: 14
ashland ky. us
200 amp service, in a strip mall,200 amp disconnect at meter base. service panel about 100 ft. away is there a code requiring a main breaker in the service panel? and if not would you do ?


kenrod3020
2017 / 2014 NEC & Related Books and Study Guides
Re: service disconnects #80366
04/04/02 08:41 AM
04/04/02 08:41 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,274
Fullerton, CA USA
There's not a requirement for an additional disconnecting means at the subpanel.
As long as the main breaker at the meter base is accessible to the occupant per 240.24(B), and 230.72(C) I would just use a main-lug-only subpanel.
If it's one of those places that (in violation) keeps an electrical room locked from the occupants, I'd probably add the main.

[This message has been edited by electure (edited 04-06-2002).]

Re: service disconnects #80367
04/13/02 12:32 PM
04/13/02 12:32 PM
T
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
How would supplying a main breaker in the panel address the requirement in 225.35 for occupant access to the supply disconnecting means?
--
Tom

225.35 Access to Occupants.
In a multiple-occupancy building, each occupant shall have access to the occupant?s supply disconnecting means.


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Popular Topics(Views)
249,455 Are you busy
187,375 Re: Forum
176,715 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9506 MB (Peak: 1.0759 MB) Zlib enabled. Server Time: 2018-09-25 15:41:51 UTC