#80365 04/03/02 11:17 PM
Joined: Feb 2002
Posts: 14
K
Member
200 amp service, in a strip mall,200 amp disconnect at meter base. service panel about 100 ft. away is there a code requiring a main breaker in the service panel? and if not would you do ?


kenrod3020
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#80366 04/04/02 08:41 AM
Joined: Dec 2000
Posts: 4,289
Member
There's not a requirement for an additional disconnecting means at the subpanel.
As long as the main breaker at the meter base is accessible to the occupant per 240.24(B), and 230.72(C) I would just use a main-lug-only subpanel.
If it's one of those places that (in violation) keeps an electrical room locked from the occupants, I'd probably add the main.

[This message has been edited by electure (edited 04-06-2002).]

#80367 04/13/02 12:32 PM
Joined: Mar 2001
Posts: 345
T
Member
How would supplying a main breaker in the panel address the requirement in 225.35 for occupant access to the supply disconnecting means?
--
Tom

225.35 Access to Occupants.
In a multiple-occupancy building, each occupant shall have access to the occupant?s supply disconnecting means.


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,289
Joined: December 2000
Top Posters(30 Days)
dsk 3
Popular Topics(Views)
297,409 Are you busy
228,264 Re: Forum
213,161 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5