#80365 04/03/02 11:17 PM
Joined: Feb 2002
Posts: 14
K
Member
200 amp service, in a strip mall,200 amp disconnect at meter base. service panel about 100 ft. away is there a code requiring a main breaker in the service panel? and if not would you do ?


kenrod3020
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#80366 04/04/02 08:41 AM
Joined: Dec 2000
Posts: 4,294
Member
There's not a requirement for an additional disconnecting means at the subpanel.
As long as the main breaker at the meter base is accessible to the occupant per 240.24(B), and 230.72(C) I would just use a main-lug-only subpanel.
If it's one of those places that (in violation) keeps an electrical room locked from the occupants, I'd probably add the main.

[This message has been edited by electure (edited 04-06-2002).]

#80367 04/13/02 12:32 PM
Joined: Mar 2001
Posts: 345
T
Member
How would supplying a main breaker in the panel address the requirement in 225.35 for occupant access to the supply disconnecting means?
--
Tom

225.35 Access to Occupants.
In a multiple-occupancy building, each occupant shall have access to the occupant?s supply disconnecting means.


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison