Best wiring method for Horse Barn #79612 01/08/02 09:59 PM
Joined: May 2001
Posts: 129
F
frodo Offline OP
Member
hi,
what is the best wiring method for a horse barn? weatherproof everything?

how about the overhead service drop from the main load center on the pole to the barn? doesnt this have to be a quadraplex cable? (insulated neutral)..

what about grounding at the pole with no water line available? two ground rods? connected together or seperately?

thanks

frodo

2017 / 2014 NEC & Related Books and Study Guides
Re: Best wiring method for Horse Barn #79613 01/08/02 10:11 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
Hi frodo

yes
yes
not sure what U mean there..?

obviously, you've gone thru 547..

As a horse dad add..crib-proof & tantrum-proof, double it for a pony.

Re: Best wiring method for Horse Barn #79614 01/08/02 11:02 PM
Joined: May 2001
Posts: 129
F
frodo Offline OP
Member
hi,
i installed a 200A Loadcenter on a pole. from the loadcenter off a 40A double pole using #4 quadraplex. they go through a 1 1/4 emt out a weather head over to a barn into a 125 loadcenter with a 40A main. i am bringing a quadraplex over for two reasons; 1) it brings my ground over from the pole. 2) i get an insulated neutral. i drove a single ground rod at the barn.

what do I need at the service for grounding? there is no water line. i figured i would drive two ground rods.

will this satisfy the code?

if i use two ground rods 6 feet apart, do the rods have to be tied together or have a seperate run of #6 from each rod?

i am planning on using emt and fs boxes to install switches and lighting in the barn. this is the best method i can think of.

thanks for all the input..

frodo

Re: Best wiring method for Horse Barn #79615 01/09/02 03:04 AM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline
Member
See Article 547 in the NEC.

[This message has been edited by Joe Tedesco (edited 02-04-2002).]


Joe Tedesco, NEC Consultant
Re: Best wiring method for Horse Barn #79616 01/09/02 07:52 AM
Joined: May 2001
Posts: 129
F
frodo Offline OP
Member
hi,
thanks for all the input, its good to have a plce to go to for friendly discussions and advice.

-regards

frodo

Re: Best wiring method for Horse Barn #79617 01/09/02 11:06 AM
Joined: Nov 2000
Posts: 2,236
sparky66wv Offline
Member
May I suggest PVC FS boxes and PVC rigid pipe (sched 80 where needed) rather than ferrous metal?

Corrosive environment, No?


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Best wiring method for Horse Barn #79618 01/09/02 02:37 PM
Joined: Mar 2001
Posts: 345
T
tdhorne Offline
Member
Frodo Wrote:
"i installed a 200A Loadcenter on a pole. from the loadcenter off a 40A double pole using #4 quadraplex. they go through a 1 1/4 emt out a weather head over to a barn into a 125 loadcenter with a 40A main. i am bringing a quadraplex over for two reasons; 1) it brings my ground over from the pole. 2) i get an insulated neutral. i drove a single ground rod at the barn.

what do I need at the service for grounding? there is no water line. i figured i would drive two ground rods.

will this satisfy the code?

if i use two ground rods 6 feet apart, do the rods have to be tied together or have a seperate run of #6 from each rod?

i am planning on using emt and fs boxes to install switches and lighting in the barn. this is the best method i can think of.

thanks for all the input.."

Frodo
Which edition of the NEC are you working with in your area? That effects the answers a lot. For 1996 you are fine so far, for 1999 you need two rods at each building. In either case you can run one Grounding Electrode Conductor (GEC) to the first ground rod through the acorn clamp and on to the acorn clamp of the second ground rod. If you are using solid state controlled equipment in any of these buildings then you may want to get a lot more fussy about the grounding then the code requires. If you have a drilled water well within reach of any of these buildings consider running a GEC to it.
--
Tom


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Re: Best wiring method for Horse Barn #79619 01/10/02 09:43 PM
Joined: May 2001
Posts: 129
F
frodo Offline OP
Member
hi,
my area recognizes the 1999 code. on a seperate building, detached garage etc., where no ground conductor has been run then two ground rods may be required but where a egc is run with the conductors do you still need two ground rods?

i always run a ground conductor from the service to the building or detached garage to keep from having to drive two rods.

i have passed a few inspections with only one ground rod at the detached garage or building as long as i have the ground run with the feeder.

thanks

frodo

Re: Best wiring method for Horse Barn #79620 01/10/02 09:48 PM
Joined: May 2001
Posts: 129
F
frodo Offline OP
Member
hi,
pvc is a consideration. is it cost effective vs emt?

-regards

frodo

Re: Best wiring method for Horse Barn #79621 01/10/02 10:53 PM
Joined: Nov 2000
Posts: 2,236
sparky66wv Offline
Member
I show 1/2" EMT @ $0.16 per foot and 1/2" PVC at $0.18, plus the fittings are a little more expensive and the PVC conduit requires 3.3 times as many straps, but in the long run, it will hold up to the test of time. EMT will eventually rust out in an agricutural environment.

Care must be taken to provide for temperature expansion and contraction of the PVC pipe, using "frosties" or other expansion type joints.


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 99
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,022 Are you busy
205,030 Re: Forum
193,139 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3